Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

PreserveVariables


SEMN Dec 19, 2012 03:29 PM

I am trying to use the "PreserveVariables" function, and have run into a problem with two of my variables. I am using a CR800 to control an ISCO sampler on a time based sampling scheme. To do this, I am using a timer and pulse counter as public variables:
Public ISCO_Pulse_Counter
Public ISCODelayTime

I need to use the PreserveVariables function in order to maintain my stage offset, however, this function essentially freezes my sampling routine. I can think of 2 options, but am open to any suggestions.

1. Deteremine a way, if possible, to keep ISCO_Pulse_Counter and ISCODelayTime active (somehow separate them from the "PreserveVariables" function.
2. Somehow move my Constants into public fields, however, I still want to manipulate the fields as needed, and have deault values in place.

Does anyone have suggestions?

Thanks

Here is my program:

'CR800
'Declare Constants
ConstTable
Const ISCO_TIMER = 1
Const ETI_Interval = 36000 'seconds
Const ETI_Pulses = 96 '1 sample per hour * 96 times = 4 day ETI
EndConstTable

'Declare Variables and Units
Public Batt_Volt
Public Act_stage
Public STGADJ
Public Cr800Temp_C
Public CS450_Stg
Public SFSTG_ft
Public Stage_avg
Public CS450(2)
Public CS650(3)
Public StageTimerActive As Boolean
Public ISCO_Pulse_Counter
Public ISCODelayTime

Alias CS450(1)=CS450_PS
Alias CS450(2)=CS450_WTemp

Alias CS650(1)=VolWatCon
Alias CS650(2)=ElecCondu
Alias CS650(3)=SoiltTemp

Units Batt_Volt=Volts
Units Cr800Temp_C=Deg C
Units CS450_Stg=feet
Units SFSTG_ft=feet
Units Stage_avg=feet
Units VolWatCon=m^3/m^3
Units ElecCondu=ds/m
Units SoiltTemp=C

Dim LogerTime(10)
'1 - Year, 2 - Month, 3 - Day of Month, 4 - Hour, 5 - Minute
'6 - Second, 7 - Microsecond, 8 - Day Of Week (Sunday = 1), 9 - Day of Yea

'Define Data Tables
DataTable(SR3_ETI_FLOW10,True,-1)
DataInterval(0,10,Min,10)
Average (1,Cr800Temp_C,FP2,False)
Average(1,SFSTG_ft,IEEE4,False)
Average(1,Stage_avg,IEEE4,False)
Average (3,CS650(),FP2,False)
Minimum(1,Batt_Volt,FP2,False,False)
EndTable

DataTable (ETI_SampleOut, 1, -1)
DataInterval (0, 0, Sec, 0)
Sample (1, ISCO_Pulse_Counter, FP2)
EndTable

PreserveVariables

'Main Program
BeginProg
Scan(60,Sec,1,0)
SW12 (1 )
'Default Datalogger Battery Voltage measurement Batt_Volt:
Battery(Batt_Volt)
'Wiring Panel Temperature measurement PTemp_C
PanelTemp(Cr800Temp_C,_60Hz)
'CS650 Soil Moisture Probe Generic SDI-12 Sensor measurements VolWatCon, ElecCondu, SoiltTemp,
SDI12Recorder(CS650(),3,"0","M!",1,0)
'CS450 Pressure Transducer Generic SDI-12 Sensor measurements
SDI12Recorder (CS450,1,0,"M!",1.0,0)
'Convert PS to Stage (ft)
CS450_Stg=(CS450_PS)*2.31

'Allows for stage offset to be adjusted
SFSTG_ft= (CS450_Stg) + (STGADJ)
'Calculate 15 minute average stage to activate samplers
AvgRun (Stage_avg,1,SFSTG_ft,10)

'ETI Sampling Routine
If NOT StageTimerActive Then
If (Stage_avg >= Act_stage) Then
'pulse the port
WriteIO (&B10,&B10) 'same as PortSet(2,1), but for conditional control
Delay(1,1,Sec)
WriteIO (&B10,&B00) 'same as PortSet(2,0), but for conditional control
'Increment Isco pulse counter
ISCO_Pulse_Counter = 1
CallTable ETI_SampleOut
'reset the Timer
Timer(ISCO_TIMER,Sec,2)
'Start the Timer
'Activate Stage Timer
StageTimerActive = True
EndIf

Else ' Once the Stage Timer is activated
'Read Timer
ISCODelayTime = Timer(ISCO_TIMER,Sec,4)
'After 1 hour,
If ISCODelayTime > ETI_Interval Then
'pulse the port
WriteIO (&B10,&B10) 'same as PortSet(2,1), but for conditional control
Delay(1,1,Sec)
WriteIO (&B10,&B00) 'same as PortSet(2,0), but for conditional control
'Increment Isco pulse counter
ISCO_Pulse_Counter = ISCO_Pulse_Counter+ 1
CallTable ETI_SampleOut
'reset the Timer
Timer(ISCO_TIMER,Sec,2)
EndIf
EndIf

'AFter desired number of samples collected, stop pulsing
If (ISCO_Pulse_Counter >= ETI_Pulses) Then
'Clear the StageTimerActive (stops hourly pulsing continuing)
StageTimerActive = False
'Stop and clear the timer
Timer(ISCO_TIMER,Sec,3)
ISCO_Pulse_Counter = 0
ISCODelayTime = 0
EndIf

CallTable(SR3_ETI_FLOW10)

NextScan
EndProg


Danaw Dec 19, 2012 04:50 PM

Instead of PreserveVariables, you might want to look into using the CalFile instruction, which will write values out to a file or read them back in.

So you could set your stage offset and write those out to a CalFile. Then write some "run once" code to read those values back in.

Dana W.

Log in or register to post/reply in the forum.