Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

FRUN Language


SEMN May 11, 2016 03:49 PM

Hello,

I am writing a program to calculate stage in a water control structure.

We have been using a FRun sequence to enter the actual field stage value into the public table, and the logger was updating the offset if it was needed.  This has worked great:

 'Offset calculation 'Offset_SG'
  If FRun=0 Then
   Staff_Gage_Obs=0
   FRun=1
  EndIf
  Changed=Staff_Gage_Obs-Old
  If Changed=0 Then
   Stage=CS450_Stg+Offset_SG
  Else
   Offset_SG=Staff_Gage_Obs-CS450_Stg
   Stage=CS450_Stg+Offset_SG
   Old=Staff_Gage_Obs
  EndIf

We are trying to modifiy this code to enter a tape down measurement (instead of stage) to have it auto correct the offset.

I modified the following code:

   'Offset calculation 'BR2 Out Stage Offset'
  If FRun_BR2Out=0 Then
   (BR2_RP_to_Vnotch-Obs_TD_BR2Out)=0
   FRun_BR2Out=1
  EndIf
  Changed_BR2Out=(BR2_RP_to_Vnotch - Obs_TD_BR2Out)-Old_BR2Out
  If Changed_BR2Out=0 Then
   Stage_BR2Out=Raw_Level_ft_BR2Out+Offset_TD_BR2Out
  Else
   Offset_TD_BR2Out=(BR2_RP_to_Vnotch - Obs_TD_BR2Out)-Raw_Level_ft_BR2Out
   Stage_BR2Out=Raw_Level_ft_BR2Out+Offset_TD_BR2Out
   Old_BR2Out=(BR2_RP_to_Vnotch - Obs_TD_BR2Out)
  EndIf 

Where:

BR2_RP_to_Vnotch  = Our reference point fromt he top of the control structure

Obs_TD_BR2Out = our distance to water

I am getting an "Invalid or out of place expression" for the 2nd line of the revised code:    (BR2_RP_to_Vnotch-Obs_TD_BR2Out)=0

We would like to use this sequence as opposed to having field staff manually calcualte an offset.  Is there a fix to this, or a better way to procede?

Thanks


Danaw May 12, 2016 09:07 PM

You need to store your calculated expression into a variable first:

Public NewVar

newvar=BR2_RP_to_VNotch - Obs_td_br2out

newvar=0

Dana W. 

Log in or register to post/reply in the forum.